You are placing two 423 mm (19 in) relay racks with a 152 mm (6 in) vertical management panel on each end and a 12 in vertical cable management panel between the racks. The rack lineup begins against a wall in the room. What is the MINIMUM room size required?

Nội dung câu hỏi

You are placing two 423 mm (19 in) relay racks with a 152 mm (6 in) vertical management panel on each end and a 12 in vertical cable management panel between the racks. The rack lineup begins against a wall in the room. What is the MINIMUM room size required?

Các lựa chọn

Đáp án được giữ gọn theo nhãn A, B, C, D trong phần bình chọn tương tác.

  1. A. 1.83 m (6 ft) x 2.4 m (8 ft)
  2. B. 2.1 m (7 ft) x 2.4 m (8 ft)
  3. C. 2.4 m (8 ft) x 2.4 m (8 ft)
  4. D. 2.4 m (8 ft) x 3.0 m (10 ft) — đáp án hiện tại
  5. E. 3.0 m (10 ft) x 3.0 m (10 ft)