Câu 9: RCDD-001: BICSI Registered Communications Distribution Designer - RCDD
You are placing two 423 mm (19 in) relay racks with a 152 mm (6 in) vertical management panel on each end and a 12 in vertical cable management panel between the racks. The rack lineup begins against a wall in the room. What is the MINIMUM room size required?
Nội dung câu hỏi
You are placing two 423 mm (19 in) relay racks with a 152 mm (6 in) vertical management panel on each end and a 12 in vertical cable management panel between the racks. The rack lineup begins against a wall in the room. What is the MINIMUM room size required?
Các lựa chọn
Đáp án được giữ gọn theo nhãn A, B, C, D trong phần bình chọn tương tác.
- A. 1.83 m (6 ft) x 2.4 m (8 ft)
- B. 2.1 m (7 ft) x 2.4 m (8 ft)
- C. 2.4 m (8 ft) x 2.4 m (8 ft)
- D. 2.4 m (8 ft) x 3.0 m (10 ft) — đáp án hiện tại
- E. 3.0 m (10 ft) x 3.0 m (10 ft)