An ICT distribution designer is providing labeling for a data center room number 2A, located on the second floor having 10 rows of cabinets. Which of the following identifiers/labels would the designer attach to the bonding and grounding conductor between the first cabinet in the 6th row and the data center ground bar?

Nội dung câu hỏi

An ICT distribution designer is providing labeling for a data center room number 2A, located on the second floor having 10 rows of cabinets. Which of the following identifiers/labels would the designer attach to the bonding and grounding conductor between the first cabinet in the 6th row and the data center ground bar?

Các lựa chọn

Đáp án được giữ gọn theo nhãn A, B, C, D trong phần bình chọn tương tác.

  1. A. 2A/R601.1
  2. B. 2A-SBB/R601.1 — đáp án hiện tại
  3. C. 2/R6
  4. D. TEF1/R601.1