CertyRush
Đang tải...
C CertyRush
Câu hỏi free preview

Câu 120: SK0-005: CompTIA Server+ Certification Exam

SIMULATION -A recent power outage caused email services to go down. A server administrator also received averts from the datacenter's UP S. After some investigation, the server administrator learned that each PDU was rated at a maximum of 12 A. Instructions -Ensure power redundancy is implemented throughout each rack…

Nội dung câu hỏi

SIMULATION -A recent power outage caused email services to go down. A server administrator also received averts from the datacenter's UP S. After some investigation, the server administrator learned that each PDU was rated at a maximum of 12 A. Instructions -Ensure power redundancy is implemented throughout each rack and UPS alarms are resolved. Ensure the maximum potential PDU consumption does not exceed80% (or 9.6A).a. PDU selections must be changed using the penal icon.b. VM Hosts 1 and 2 and Mall Relay can be moved between racks. c. Certain devices contain additional details. If at any time you would like to bring back the initial state of the simulation, please click the Reset All button.

Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi Minh họa câu hỏi

Các lựa chọn

Đáp án được giữ gọn theo nhãn A, B, C, D trong phần bình chọn tương tác.

  1. A. See explanation below. 1. Mailrelay - Keep the mail relay on the existing Rack1 and change the primary power supply to PDU-B and Failover powersupply as PDU B. 2. Move the VM Host 1 and VM Host2 to Rack2. Assign primary power supply PDU A to VM host1 Assign Failover power supply PDU B to VM host1 Assign primary power supply PDU B to VM host2 Assign Failover power supply PDU A to VM host2 — đáp án hiện tại

Cộng đồng

0 bình luận công khai. Tên thành viên được ẩn một phần.

Chưa có bình luận. Mở giao diện tương tác để bắt đầu thảo luận.

Câu hỏi liền kề