Câu 1: CDCS: Certified Data Centre Specialist

A 5kW (power consumption) server keeps crashing with the message ‘temperature too high’.- The intake temperature is measured at 25 °C/77 °F and a relative humidity (RH) level of 50%.- The exhaust temperature is 29 °C/84 °F and 45% RH.- The raised floor is providing adequate amount of CFM/CMH at a reasonable velocity.-…

Nội dung câu hỏi

A 5kW (power consumption) server keeps crashing with the message ‘temperature too high’.- The intake temperature is measured at 25 °C/77 °F and a relative humidity (RH) level of 50%.- The exhaust temperature is 29 °C/84 °F and 45% RH.- The raised floor is providing adequate amount of CFM/CMH at a reasonable velocity.- The pressure under the raised floor is approximately 25 Pa/0.1 inch H20. Analyze the situation and indicate what the most likely cause is for this server to crash.

Các lựa chọn

Đáp án được giữ gọn theo nhãn A, B, C, D trong phần bình chọn tương tác.

  1. A. Dust inside the server causing issues with convection-based heat transfer — đáp án hiện tại
  2. B. The exhaust temperature is exceeding the ASHRAE recommended values
  3. C. The raised floor pressure is too low and/or the raised floor tile % opening is not adequate
  4. D. No cause could be determined as the CFM/CMH of the air conditioning equipment is not stated