Câu 10: CDCS: Certified Data Centre Specialist

You are allowed to use a calculator for this question.- A computer room has a net volume of approximately 2,500 m3/88,287 ft3.- The temperature is 20 °C/68 °F.- The required design concentration is 7%.- The S-Factor is 0.1359 (metric)/1.885 (imperial). Calculate the amount of gas required for this computer room based…

Nội dung câu hỏi

You are allowed to use a calculator for this question.- A computer room has a net volume of approximately 2,500 m3/88,287 ft3.- The temperature is 20 °C/68 °F.- The required design concentration is 7%.- The S-Factor is 0.1359 (metric)/1.885 (imperial). Calculate the amount of gas required for this computer room based on FM200. What is the correct weight?

Các lựa chọn

Đáp án được giữ gọn theo nhãn A, B, C, D trong phần bình chọn tương tác.

  1. A. Approximately 410 kg/900 lbs — đáp án hiện tại
  2. B. Approximately 820 kg/1,800 lbs
  3. C. Approximately 1,390 kg/3,000 lbs
  4. D. Approximately 1,640 kg/3,600 lbs